My father is closing up his basement shop so they can move into a smaller condo. I am "taking care" of his tools in my shop. I got the Delta dust collector home a few weeks ago and went to start it up and it is blowing the circuit breaker. It is a 1.5hp 12 amp motor. I have put it on a 15 amp isolated (nothing else on it) circuit and a 20 amp isolated circuit. It starts to engage for a second, then pops the breaker and spins down.

Any advice on how I can go about troubleshooting this?
 
Signed-In Members Don't See This Ad
Is this a 120 volt motor or a 220 volt motor setup??? What are you doing to energise it. Is this a plug in or hardwired??? What type breaker (Brand) and what is the model # on the dust collector??? How far is the panel from the dust collector???

15 amp breaker is a no-no.
 
Last edited:
Russ; I would find someone with a clamp on amp probe and see what the motor is pulling on start up. I bet it will be north of 30-40 amps or more. If your motor doesn't reach full speed in a second or two, it will pop the breaker. Take the impeller off the motor shaft and take another reading. If it still pops the breaker, you may have dry or bad bearings if it hasn't been used in a while. Most modern motors have sealed bearings, so you can't lube them. You could run a 30 amp breaker if you use #10 wire, or you could wire the motor for 220 volts if it allows you to do so. Usualy a 1.5 hp motor will be made to run both voltages. There should be a diagram on the motor plate that tells you how to connect the wires for both voltages. On a 120V motor you should have a black, white, and a green wire for your leads. On a 220V motor you should have a black and red for your leads and maybe a green to ground the motor back to the box. Make sure the motor turns freely by hand with no drag or bearing noise. Also check for a bent shaft. I run a 120V 1.5 hp motor on a 20 amp breaker on my main vac system. If I don't use it for a while, or I start it when the shop is cold, it may trip the breaher several times before it will keep running. Same with my contractor table saw. Also if your motor is a capacitor start, that may be bad. Jim S
 
Last edited:
I would start out by making sure it isn't wired for 220 volts. Then I would take the cover off the blower and make sure it moved freely. I would do both of these before I tried plugging it back in. A motor has very little resistance until it starts to turn. If the blower is not moving freely it could be that when you turn on the power to the unit and it doesn't start to turn it just draws too much current and blows the breaker. Anyway it is worth a try to check these simple things!
 
Thank you guys for the quick replys.

I wil check the model# this weekend when I get back from camping with the Scouts.

It is 120 plug in. To turn it on I just press the big green button. it does sound like there is a bit of a drag on the motor. On Sunday I am going to take the front plate off and see if there is anything caked on the impeller or the encasement. The collector is about 30' from the panel. I was also thinking about putting it onto my generator, that has a free 30 amp circuit on it to see if I can get it to spin up. The generator also has a 220 port, but the collector is not currently wired for it.

Jim, that you for the probe suggestion, a friend of mine has a clamp on probe that he is going to bring over.

I will let you know what I find on Monday.
 